Electric wire question for Electricians #8371387 09/01/21 05:01 PM
Joined: Jul 2011
Posts: 1,491
B
BearkatHunter2011 Offline OP
Pro Tracker
OP Offline
Pro Tracker
B
Joined: Jul 2011
Posts: 1,491
Do I need conduit?

I'm going to run aluminum URD 4/0 cable to provide power to my shop from a pedestal transformer. Although this is direct burial wire, do I need to encase it in conduit due to fireants?

Thanks.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371401 09/01/21 05:13 PM
Joined: Oct 2006
Posts: 18,556
D
ducknbass Online Content
THF Celebrity
Online Content
THF Celebrity
D
Joined: Oct 2006
Posts: 18,556
If it’s direct burial no.

Fire ants will only get to it if it’s cut.

I personally would never run direct burial aluminum though. We’ll direct burial at all.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371407 09/01/21 05:16 PM
Joined: Oct 2004
Posts: 39,549
R
redchevy Offline
THF Celebrity
Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,549
Ran dirrect burial from my parents house to the smoke hose in the back yard about 25 years ago. No problems yet, it was coper wire though. Also ran some of the same stuff to a pole barn at the ranch, same no issues with it as well.


It's hell eatin em live
Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371469 09/01/21 06:05 PM
Joined: Jul 2011
Posts: 9,972
O
Old Rabbit Online Content
THF Trophy Hunter
Online Content
THF Trophy Hunter
O
Joined: Jul 2011
Posts: 9,972
I would be more worried about gophers. They may not be a problem where you live, but in East Texas, they love to chew on electric wires.

Re: Electric wire question for Electricians [Re: ducknbass] #8371496 09/01/21 06:29 PM
Joined: Aug 2009
Posts: 22,716
B
BigPig Offline
THF Celebrity
Offline
THF Celebrity
B
Joined: Aug 2009
Posts: 22,716
Originally Posted by BearkatHunter2011
Do I need conduit?

I'm going to run aluminum URD 4/0 cable to provide power to my shop from a pedestal transformer. Although this is direct burial wire, do I need to encase it in conduit due to fireants?

Thanks.


No. Is it going to be near any other lines? Water lines? Gas lines?

Originally Posted by ducknbass
If it’s direct burial no.

Fire ants will only get to it if it’s cut.

I personally would never run direct burial aluminum though. We’ll direct burial at all.


I wouldn’t run direct burial anything moving over 20amps, that’s just me. You have to go a lot deeper if you’re running direct burial service wire.

The aluminum is fine, and a better conductor than copper for what you’re running, also a lot cheaper.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371500 09/01/21 06:30 PM
Joined: May 2011
Posts: 28,031
skinnerback Offline
THF Celebrity Chef
Offline
THF Celebrity Chef
Joined: May 2011
Posts: 28,031
Originally Posted by BearkatHunter2011
Do I need conduit?

I'm going to run aluminum URD 4/0 cable to provide power to my shop from a pedestal transformer. Although this is direct burial wire, do I need to encase it in conduit due to fireants?

Thanks.



What dunknbass said. Answer is no, just bury it deep and would run copper vs aluminum.

I DO recommend only using PVC Conduit where the cable comes out on each end, to protect it from lawnmowers & weed eaters.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371501 09/01/21 06:31 PM
Joined: Oct 2004
Posts: 39,549
R
redchevy Offline
THF Celebrity
Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,549
Interesting, Ive never heard of aluminum referred to as a better conductor than copper or really better than anything electric related.


It's hell eatin em live
Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371516 09/01/21 06:41 PM
Joined: Sep 2013
Posts: 1,593
Opening Day Offline
Pro Tracker
Offline
Pro Tracker
Joined: Sep 2013
Posts: 1,593
I would put in conduit

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371528 09/01/21 06:55 PM
Joined: Jan 2014
Posts: 12,765
P
Paluxy Online Content
THF Celebrity
Online Content
THF Celebrity
P
Joined: Jan 2014
Posts: 12,765
If the pedestal transformer is from the power company they will require conduit unless the meter is at the pedestal.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371604 09/01/21 08:21 PM
Joined: Jul 2011
Posts: 1,491
B
BearkatHunter2011 Offline OP
Pro Tracker
OP Offline
Pro Tracker
B
Joined: Jul 2011
Posts: 1,491
Yes, the meter is at the pedestal.

No gophers in our neck of the woods. I'm guessing because of the heavy black clay.

I was at least going to put the last 10 feet of each end in conduit with 90's up to the meter box on one end and the breaker box in the barn.

No other water lines or gas lines in the vicinity. This is out in the county. Connecting a meter on a pedestal (near my light pole and existing transformer) and running 300 feet to a barn that will soon be getting a concrete floor and turned into a shop for FFA projects.

I agree that I would prefer copper but WOW it is high right now.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371619 09/01/21 08:28 PM
Joined: Jun 2020
Posts: 325
G
Giblett Offline
Bird Dog
Offline
Bird Dog
G
Joined: Jun 2020
Posts: 325
I would put it in conduit. If it ever messes up it's a whole lot easier to pull wire than dig a ditch.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371622 09/01/21 08:28 PM
Joined: Aug 2009
Posts: 22,716
B
BigPig Offline
THF Celebrity
Offline
THF Celebrity
B
Joined: Aug 2009
Posts: 22,716
Originally Posted by BearkatHunter2011
Yes, the meter is at the pedestal.

No gophers in our neck of the woods. I'm guessing because of the heavy black clay.

I was at least going to put the last 10 feet of each end in conduit with 90's up to the meter box on one end and the breaker box in the barn.

No other water lines or gas lines in the vicinity. This is out in the county. Connecting a meter on a pedestal (near my light pole and existing transformer) and running 300 feet to a barn that will soon be getting a concrete floor and turned into a shop for FFA projects.

I agree that I would prefer copper but WOW it is high right now.


Copper has been high. I ran aluminum last year, bought 150 feet of it for $1,050 vs copper being $2,995 and had to buy 200 feet so I would’ve been stuck with lots of expensive waste.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371626 09/01/21 08:30 PM
Joined: Jun 2020
Posts: 325
G
Giblett Offline
Bird Dog
Offline
Bird Dog
G
Joined: Jun 2020
Posts: 325
I would put it in conduit. If it ever messes up it's a whole lot easier to pull wire than dig a ditch.

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371766 09/01/21 10:37 PM
Joined: May 2009
Posts: 1,867
G
Grit Online Content
Pro Tracker
Online Content
Pro Tracker
G
Joined: May 2009
Posts: 1,867
I just repaired an underground feeder (UF 12-2) out to my bunkhouse. We had our placed cleared around the house and he cut the line. All my fault as I didn't know exactly where it was buried. But the building is powered off a live plug and has a dedicated panel. But the UF cable is only covered in conduit on both ends and about a couple feet in the ground. The rest of the cable is direct burial.

Last edited by Grit; 09/01/21 10:41 PM.

Garrett
Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8371767 09/01/21 10:38 PM
Joined: Apr 2009
Posts: 6,109
P
pdr55 Online Content
THF Trophy Hunter
Online Content
THF Trophy Hunter
P
Joined: Apr 2009
Posts: 6,109
If it was mine I would run it in conduit.


If you`re running down my country, man,
You`re walking on the fighting side of me. (Merle)
Re: Electric wire question for Electricians [Re: redchevy] #8371775 09/01/21 10:51 PM
Joined: Feb 2019
Posts: 1,440
P
Poppa Offline
Pro Tracker
Offline
Pro Tracker
P
Joined: Feb 2019
Posts: 1,440
Originally Posted by redchevy
Interesting, Ive never heard of aluminum referred to as a better conductor than copper or really better than anything electric related.

me neither. why would the nec require bigger Al wire for the same ampacity of Cu? i ran # 2 direct burial to a shop/apartment. its on a 125 amp breaker and feeds a 200 amp panel with a 70 amp sub panel for the shop. 6 yrs old, no problems. It is what farmers electric coop told me to do in conjunction with the electrician i used.

Last edited by Poppa; 09/01/21 11:12 PM. Reason: k
Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8372082 09/02/21 03:10 AM
Joined: Dec 2012
Posts: 11,913
S
Simple Searcher Online Content
THF Celebrity
Online Content
THF Celebrity
S
Joined: Dec 2012
Posts: 11,913
I agree with most here, run it in conduit. Aluminum is good.
How long of a run are you doing?


[Linked Image]

"Man is still a hunter, still a simple searcher after meat..." Robert C. Ruark
Re: Electric wire question for Electricians [Re: redchevy] #8372189 09/02/21 10:36 AM
Joined: Oct 2006
Posts: 18,556
D
ducknbass Online Content
THF Celebrity
Online Content
THF Celebrity
D
Joined: Oct 2006
Posts: 18,556
Originally Posted by redchevy
Interesting, Ive never heard of aluminum referred to as a better conductor than copper or really better than anything electric related.



Because it’s not. roflmao

Re: Electric wire question for Electricians [Re: redchevy] #8372206 09/02/21 11:03 AM
Joined: Aug 2009
Posts: 22,716
B
BigPig Offline
THF Celebrity
Offline
THF Celebrity
B
Joined: Aug 2009
Posts: 22,716
Originally Posted by redchevy
Interesting, Ive never heard of aluminum referred to as a better conductor than copper or really better than anything electric related.


Maybe conductor wasn’t the wording I was going for. Aluminum for service cable can be just as good as copper, although you’ll have to step up in size some, but it’s lighter and easier to work with being it flexes easier than copper. We had some right turns when going from house to shop, copper would’ve never made those turns.

Re: Electric wire question for Electricians [Re: BigPig] #8372367 09/02/21 01:46 PM
Joined: Dec 2012
Posts: 11,913
S
Simple Searcher Online Content
THF Celebrity
Online Content
THF Celebrity
S
Joined: Dec 2012
Posts: 11,913
Originally Posted by BigPig
Originally Posted by redchevy
Interesting, Ive never heard of aluminum referred to as a better conductor than copper or really better than anything electric related.


Maybe conductor wasn’t the wording I was going for. Aluminum for service cable can be just as good as copper, although you’ll have to step up in size some, but it’s lighter and easier to work with being it flexes easier than copper. We had some right turns when going from house to shop, copper would’ve never made those turns.


I read through your statement of aluminum being a better conductor and I pretty much figured out what you meant, so I left it alone.
But pulling aluminum or copper through a conduit that is installed by code (max 360 degree of bends, minimum radius, etc) it makes no difference, they both will pull. Truth be known that the normal insulation on copper, THHN, is much slicker and will pull easier than aluminum. Weight and cost is about the only disadvantage of copper.


[Linked Image]

"Man is still a hunter, still a simple searcher after meat..." Robert C. Ruark
Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8372374 09/02/21 01:52 PM
Joined: Nov 2007
Posts: 6,530
P
PappawRock Offline
THF Trophy Hunter
Offline
THF Trophy Hunter
P
Joined: Nov 2007
Posts: 6,530
Steve McQueen is one copper that made right turns plenty in Bullitt...

Re: Electric wire question for Electricians [Re: BearkatHunter2011] #8372389 09/02/21 02:00 PM
Joined: Mar 2010
Posts: 745
R
RayBob Offline
Tracker
Offline
Tracker
R
Joined: Mar 2010
Posts: 745
PVC conduit is pretty inexpensive And adds a layer of protection to your line. Everything I put in the ground here is in conduit.