Water pipe advice? #8824252 03/27/23 01:12 PM
Joined: Oct 2004
Posts: 39,524
R
redchevy Offline OP
THF Celebrity
OP Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,524
Going to be running a water line to a home site. 1300 feet in length 15-20 feet vertical rise from meter. Meter is 3/4 inch. One person has recommended we run 2 inch seemed excessive to me. What size, and what material would you recommend?


It's hell eatin em live
Re: Water pipe advice? [Re: redchevy] #8824258 03/27/23 01:21 PM
Joined: Apr 2009
Posts: 3,232
B
blkt2 Online Content
Veteran Tracker
Online Content
Veteran Tracker
B
Joined: Apr 2009
Posts: 3,232
The head of a 2" pipe full of water over that distance and rise may exceed the pressure at the meter but I would have to dust off a book to know for sure. Normally that rise would only have about 5-7 psi and I am not sure if the length of the run adds to that from friction.


Trolling? Heck no, I meant every word of it.
Re: Water pipe advice? [Re: blkt2] #8824282 03/27/23 01:45 PM
Joined: Oct 2008
Posts: 5,119
G
GUTIT Offline
THF Trophy Hunter
Offline
THF Trophy Hunter
G
Joined: Oct 2008
Posts: 5,119
Originally Posted by blkt2
The head of a 2" pipe full of water over that distance and rise may exceed the pressure at the meter but I would have to dust off a book to know for sure. Normally that rise would only have about 5-7 psi and I am not sure if the length of the run adds to that from friction.


This should be good,,,,,,,,,if you know, you know.

Red , I have a State Fire Marshall underground license, PM sent


Stronghold Construction Group
Commercial and Residential Project Management
Managing all your construction needs
Kent@StrongholdConstructionGroupDOTcom


Re: Water pipe advice? [Re: blkt2] #8824283 03/27/23 01:50 PM
Joined: Jan 2014
Posts: 12,755
P
Paluxy Online Content
THF Celebrity
Online Content
THF Celebrity
P
Joined: Jan 2014
Posts: 12,755
Originally Posted by blkt2
The head of a 2" pipe full of water over that distance and rise may exceed the pressure at the meter but I would have to dust off a book to know for sure. Normally that rise would only have about 5-7 psi and I am not sure if the length of the run adds to that from friction.


Pipe diameter has no effect on column psi.

Re: Water pipe advice? [Re: redchevy] #8824286 03/27/23 01:53 PM
Joined: Nov 2010
Posts: 3,220
M
Marc K Offline
Veteran Tracker
Offline
Veteran Tracker
M
Joined: Nov 2010
Posts: 3,220
The vertical rise will cost you around 9 psi, then you have to add friction loss which will be the larger number by far. You have to decide how much flow you need per minute. I would use around 15-20 gallons per minute or more.

Looks like 1-1/2" with 60 psi at the meter, would give you 51 psi at the house with a very small flow. As you open more faucets and increase the flow to around 20 gallons per minute, the pressure will only be 20 psi. (sinks/showers/appliances/garden hose combined)

2" makes better sense assuming schedule 40 PVC.

Link to calculator : Water Flow in pipes

Marc

Last edited by Marc K; 03/27/23 01:55 PM.

A Democracy is when two wolves and a lamb vote on the dinner menu. That is why this country was specifically not designed as a Democracy. We are a Constitutional Republic.
Re: Water pipe advice? [Re: redchevy] #8824305 03/27/23 02:22 PM
Joined: Oct 2004
Posts: 39,524
R
redchevy Offline OP
THF Celebrity
OP Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,524
There is a regulator at the meter but believe they have 90 psi plus at the meter.


It's hell eatin em live
Re: Water pipe advice? [Re: redchevy] #8824317 03/27/23 02:38 PM
Joined: Dec 2008
Posts: 41,152
J.G. Online Content
THF Celebrity
Online Content
THF Celebrity
Joined: Dec 2008
Posts: 41,152
I'd run 2" Apache pipe (from a roll) meter to house.

Head pressure loss is .434 psi per foot of elevation. So your 15-20 feet of elevation is losing almost 10 psi.

Friction loss is directly affected by pipe diameter, and gpm flowing through it. That's why fire engines carry 5" supply line. It has almost no friction loss.

I'd rather need to reduce pressure at the house, than to get there and have not enough pressure. Trenching the ditch and back filling it is all the work anyway. Might as well put in a little bit bigger pipe and be done with it.


[Linked Image]
800 Yard Steel Range
Precision Rifle Instruction
Memberships and Classes Available
Re: Water pipe advice? [Re: GUTIT] #8824322 03/27/23 02:43 PM
Joined: Sep 2004
Posts: 12,391
R
RedRanger Online Content
THF Celebrity
Online Content
THF Celebrity
R
Joined: Sep 2004
Posts: 12,391
Originally Posted by GUTIT
Originally Posted by blkt2
The head of a 2" pipe full of water over that distance and rise may exceed the pressure at the meter but I would have to dust off a book to know for sure. Normally that rise would only have about 5-7 psi and I am not sure if the length of the run adds to that from friction.


This should be good,,,,,,,,,if you know, you know.

Red , I have a State Fire Marshall underground license, PM sent


Is that fire protection sprinklers?

Re: Water pipe advice? [Re: J.G.] #8824328 03/27/23 02:47 PM
Joined: Sep 2004
Posts: 12,391
R
RedRanger Online Content
THF Celebrity
Online Content
THF Celebrity
R
Joined: Sep 2004
Posts: 12,391
Originally Posted by J.G.
I'd run 2" Apache pipe (from a roll) meter to house.

Head pressure loss is .434 psi per foot of elevation. So your 15-20 feet of elevation is losing almost 10 psi.

Friction loss is directly affected by pipe diameter, and gpm flowing through it. That's why fire engines carry 5" supply line. It has almost no friction loss.

I'd rather need to reduce pressure at the house, than to get there and have not enough pressure. Trenching the ditch and back filling it is all the work anyway. Might as well put in a little bit bigger pipe and be done with it.


Apache Pipe?

Enlightenment me, I googled and it said Apache was based in Canada and does oil and gas piping.

Correct company?

Re: Water pipe advice? [Re: redchevy] #8824373 03/27/23 04:40 PM
Joined: Oct 2004
Posts: 39,524
R
redchevy Offline OP
THF Celebrity
OP Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,524
Open to alternatives to pvc also. Someone recommended hydromaxx… I’m not sure it’s rated for potable water and if you google it make sure it has two xx’s at the end lol


It's hell eatin em live
Re: Water pipe advice? [Re: redchevy] #8824378 03/27/23 04:49 PM
Joined: Sep 2007
Posts: 4,294
oldoak2000 Offline
Extreme Tracker
Offline
Extreme Tracker
Joined: Sep 2007
Posts: 4,294
My house has 800' of 2" pvc with a 5/8" meter. I get good pressure at full-flow at the house, and no 'pressure-drop' issues with multiple faucets running water, even with a full-open water hose going.

For your 1300' and 3/4 meter you would want MINIMUM 2" line, as 1300' can equate to a ton of friction in the line at full-meter-flow rates for any smaller size main line.

The bigger pipe 'lowers friction' by reducing the velocity of the water in the pipe necessary to maintain a certain flow rate.
A smaller pipe will also INCREASE water-hammer when shutting off high-flow faucets.

Re: Water pipe advice? [Re: Paluxy] #8824379 03/27/23 04:50 PM
Joined: Mar 2010
Posts: 12,082
N
ntxtrapper Online Content
THF Celebrity
Online Content
THF Celebrity
N
Joined: Mar 2010
Posts: 12,082
Originally Posted by Paluxy
Originally Posted by blkt2
The head of a 2" pipe full of water over that distance and rise may exceed the pressure at the meter but I would have to dust off a book to know for sure. Normally that rise would only have about 5-7 psi and I am not sure if the length of the run adds to that from friction.


Pipe diameter has no effect on column psi.


Hmmm.

Re: Water pipe advice? [Re: redchevy] #8824381 03/27/23 04:53 PM
Joined: Nov 2007
Posts: 13,203
CCBIRDDOGMAN Offline
Bird Herder
Offline
Bird Herder
Joined: Nov 2007
Posts: 13,203
I thought this was gonna be question for NORML. Carry on.


Originally Posted by bill oxner
Haven't had it in years but never spit any out.


Originally Posted by bill oxner
I am a sucker for happy endings and strapped cowboys.
Re: Water pipe advice? [Re: redchevy] #8824383 03/27/23 05:09 PM
Joined: Sep 2004
Posts: 12,391
R
RedRanger Online Content
THF Celebrity
Online Content
THF Celebrity
R
Joined: Sep 2004
Posts: 12,391
Originally Posted by redchevy
Going to be running a water line to a home site. 1300 feet in length 15-20 feet vertical rise from meter. Meter is 3/4 inch. One person has recommended we run 2 inch seemed excessive to me. What size, and what material would you recommend?


2" PVC will be your best choice, 3" will just be over kill and eat you alive in cost.

PVC has like tripled in the last 2 years.

Re: Water pipe advice? [Re: CCBIRDDOGMAN] #8824426 03/27/23 06:21 PM
Joined: Nov 2009
Posts: 69,145
N
NORML as can be Offline
^^Cut the Cord^^
Offline
^^Cut the Cord^^
N
Joined: Nov 2009
Posts: 69,145
Originally Posted by CCBIRDDOGMAN
I thought this was gonna be question for NORML. Carry on.

RooR peep


(R-TX) .-- " TCNN CURL CRLB VFF VRNO AYR SNDL CGC TLRY MSOS "

_=====___=________==-



Re: Water pipe advice? [Re: redchevy] #8824440 03/27/23 06:53 PM
Joined: Oct 2004
Posts: 39,524
R
redchevy Offline OP
THF Celebrity
OP Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,524
Have located some 20 foot joints of 2”, looks like our boy.


It's hell eatin em live
Re: Water pipe advice? [Re: redchevy] #8824441 03/27/23 06:55 PM
Joined: Sep 2004
Posts: 12,391
R
RedRanger Online Content
THF Celebrity
Online Content
THF Celebrity
R
Joined: Sep 2004
Posts: 12,391
Originally Posted by redchevy
Have located some 20 foot joints of 2”, looks like our boy.


Usually only Homeo Depot and Blowes sells 10 feet stick of PVC, most supply house have 20 feet sticks......

Re: Water pipe advice? [Re: CCBIRDDOGMAN] #8824748 03/28/23 02:40 AM
Joined: Mar 2010
Posts: 12,082
N
ntxtrapper Online Content
THF Celebrity
Online Content
THF Celebrity
N
Joined: Mar 2010
Posts: 12,082
Originally Posted by CCBIRDDOGMAN
I thought this was gonna be question for NORML. Carry on.


I bet he likes a hot smoke. Just a guess.

Re: Water pipe advice? [Re: Paluxy] #8824757 03/28/23 02:53 AM
Joined: Apr 2009
Posts: 3,232
B
blkt2 Online Content
Veteran Tracker
Online Content
Veteran Tracker
B
Joined: Apr 2009
Posts: 3,232
Originally Posted by Paluxy
Originally Posted by blkt2
The head of a 2" pipe full of water over that distance and rise may exceed the pressure at the meter but I would have to dust off a book to know for sure. Normally that rise would only have about 5-7 psi and I am not sure if the length of the run adds to that from friction.


Pipe diameter has no effect on column psi.


Of course you are correct. You would think that I'd remember that since I deal with this stuff almost daily. I have never laid down a 1300 ft long run before. Do they make 2-in pex or is that just too darn expensive? I had to buy a big roll of inch and a half pex a while back and was blown away at what it cost


Trolling? Heck no, I meant every word of it.
Re: Water pipe advice? [Re: ntxtrapper] #8824759 03/28/23 03:06 AM
Joined: Nov 2009
Posts: 69,145
N
NORML as can be Offline
^^Cut the Cord^^
Offline
^^Cut the Cord^^
N
Joined: Nov 2009
Posts: 69,145
Originally Posted by ntxtrapper
Originally Posted by CCBIRDDOGMAN
I thought this was gonna be question for NORML. Carry on.


I bet he likes a hot smoke. Just a guess.

No Sir, actually I'm a joint man I never cared for pipes.. Except for the Power Hitter I had in the 70's.

They were made in Austin Texas.
[Linked Image]


(R-TX) .-- " TCNN CURL CRLB VFF VRNO AYR SNDL CGC TLRY MSOS "

_=====___=________==-



Re: Water pipe advice? [Re: redchevy] #8824825 03/28/23 12:08 PM
Joined: Dec 2008
Posts: 41,152
J.G. Online Content
THF Celebrity
Online Content
THF Celebrity
Joined: Dec 2008
Posts: 41,152
Originally Posted by redchevy
Have located some 20 foot joints of 2”, looks like our boy.


How bout a joint every 500 feet?

Unless you like extra work and expense, and more joints for potential leaks.


[Linked Image]
800 Yard Steel Range
Precision Rifle Instruction
Memberships and Classes Available
Re: Water pipe advice? [Re: J.G.] #8824829 03/28/23 12:44 PM
Joined: Dec 2009
Posts: 9,805
The Dude Abides Online Content
THF Trophy Hunter
Online Content
THF Trophy Hunter
Joined: Dec 2009
Posts: 9,805
Originally Posted by J.G.
Originally Posted by redchevy
Have located some 20 foot joints of 2”, looks like our boy.


How bout a joint every 500 feet?

Unless you like extra work and expense, and more joints for potential leaks.

[Linked Image]


Originally Posted by Superduty
I am still looking for the perfect apron, one with reinforced knee areas would be perfect.

Re: Water pipe advice? [Re: J.G.] #8824836 03/28/23 01:20 PM
Joined: Sep 2004
Posts: 12,391
R
RedRanger Online Content
THF Celebrity
Online Content
THF Celebrity
R
Joined: Sep 2004
Posts: 12,391
Originally Posted by J.G.
Originally Posted by redchevy
Have located some 20 foot joints of 2”, looks like our boy.


How bout a joint every 500 feet?

Unless you like extra work and expense, and more joints for potential leaks.


Is that the Apache pipe you are talking about?

Is it safe for potable water?

I looked on their website and don't see prices for or pipe for potable water, only for oil and gas

Apache Pipe

Re: Water pipe advice? [Re: RedRanger] #8824841 03/28/23 01:26 PM
Joined: Dec 2008
Posts: 41,152
J.G. Online Content
THF Celebrity
Online Content
THF Celebrity
Joined: Dec 2008
Posts: 41,152
Apache was going from memory of a friend of mine that put in one run of pipe, 200 yards long from meter to house. No joints except for the ends.

The black pipe on the roll is suitable for potable water.

It's like using Pex for the main service line.

Personally, I would build a dispenser that connected to the skid steer. Straddle the ditch and back up.


[Linked Image]
800 Yard Steel Range
Precision Rifle Instruction
Memberships and Classes Available
Re: Water pipe advice? [Re: J.G.] #8824843 03/28/23 01:27 PM
Joined: Oct 2004
Posts: 39,524
R
redchevy Offline OP
THF Celebrity
OP Offline
THF Celebrity
R
Joined: Oct 2004
Posts: 39,524
Originally Posted by J.G.
Originally Posted by redchevy
Have located some 20 foot joints of 2”, looks like our boy.


How bout a joint every 500 feet?

Unless you like extra work and expense, and more joints for potential leaks.

Definitely not against other products. I’m not familiar with a product. Couldn’t find much on the Apache. I also would like to stay with something that isn’t abnormal so to say want to be able to buy parts, we will be adding a few spots along the way for some hose bibs etc not sure how that would work. Plus I’ve dealt with pvc. If there is a better readily available product I would consider it for sure.


It's hell eatin em live