I need , or want to get a extension cord for a 220v compressor at home. I have a YUGE cord now, its like a inch or more in diameter . Looking for something with a smaller diameter with out burning the motor up. I only need it to go 25 and really it will be a little less than that.
240v 60hz 15 AMPS 3450 rpm ph 01 output 2.98 kw LR AMPS 93
Im looking at this one.
https://www.ebay.com/itm/Heavy-Duty-25FT-50-Amp-10-3-Welder-Extension-Cord-MIG-TIG-Plasma-220-Volt/164355076675?hash=item2644537243:g:8ncAAOSwERtfR1yh
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7967664
09/10/20 12:25 AM
|
Joined: Nov 2009
Posts: 91,416
bill oxner
THF Celebrity
|
THF Celebrity
Joined: Nov 2009
Posts: 91,416 |
Good luck. Haven't used one lately. Most things are now cordless.
Quail hunting is like walking into, and out of a beautiful painting all day long. Gene Hill
|
|
|
Re: extension cord needed for 220V compressor?
[Re: bill oxner]
#7967754
09/10/20 12:53 AM
|
Joined: Sep 2012
Posts: 15,309
Jimbo1
THF Celebrity
|
THF Celebrity
Joined: Sep 2012
Posts: 15,309 |
Good luck. Haven't used one lately. Most things are now cordless. That was helpful!
FJB - Lets Go Brandon BBB - Bring Back Better Awake - Not Woke!
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7967777
09/10/20 01:02 AM
|
Joined: Jul 2006
Posts: 110,761
dogcatcher
THF Celebrity
|
THF Celebrity
Joined: Jul 2006
Posts: 110,761 |
The one you looked at is reasonable a 50 foot roll of 10/3 is $91 at home depot, or almost $2 a foot.
Combat Infantryman, the ultimate hunter where the prey shoots back. _____________"Illegitimus non carborundum est"_______________
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7967930
09/10/20 02:42 AM
|
Joined: Nov 2009
Posts: 68,257
NORML as can be
^^Cut the Cord^^
|
^^Cut the Cord^^
Joined: Nov 2009
Posts: 68,257 |
10/2 romax and hard wire it.
(R-TX) .-- " TCNN CURL CRLB VFF VRNO AYR SNDL CGC TLRY MSOS "
_=====___=________==-
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7967969
09/10/20 03:15 AM
|
Joined: Dec 2011
Posts: 5,754
Lazyjack
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Dec 2011
Posts: 5,754 |
12/3 is really all should need. Biggest draw back with the 50 amp selected is the male and female ends. It probably will not match your compressor cord. What does you compressor female end look like, and the wall plug.
The weakest point on factory cords are the ends. I would probably build one. 12/3 cord with heavy duty orange ends. Usually available at box stores.
If you rather a store bought, look for a 20 amp 240 volt.cord. That will probably match your ends.
Also, keep as short as practical. A big mistake, often consumer buys a too long heavy cord, then coil it up. If you have 15 feet or so tightly coiled up on floor or wall, recatance due to current flow will cause voltage drop.
If the 2nd amendment was written just to include guns for hunting, why is there not an amendment to protect fishing poles?
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7967980
09/10/20 03:24 AM
|
Joined: Jan 2011
Posts: 21,367
Bullfrog
THF Celebrity
|
THF Celebrity
Joined: Jan 2011
Posts: 21,367 |
Lazyjack, you saying it’s better off strung out vs coiled up? or delete the length of unneeded wire for resistance purposes? Trying to wrap my head around that new word.
![[Linked Image]](https://krdesignsco.com/wp-content/uploads/2019/02/pig.gif) Man if I knew what Oxner knows I could throw away what I know
|
|
|
Re: extension cord needed for 220V compressor?
[Re: bill oxner]
#7968052
09/10/20 05:24 AM
|
Joined: May 2011
Posts: 27,081
skinnerback
THF Celebrity Chef
|
THF Celebrity Chef
Joined: May 2011
Posts: 27,081 |
Good luck. Haven't used one lately. Most things are now cordless. 
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Bullfrog]
#7968054
09/10/20 05:56 AM
|
Joined: May 2011
Posts: 27,081
skinnerback
THF Celebrity Chef
|
THF Celebrity Chef
Joined: May 2011
Posts: 27,081 |
Lazyjack, you saying it’s better off strung out vs coiled up? or delete the length of unneeded wire for resistance purposes? Trying to wrap my head around that new word. Lazyjack made some good points. 12/3 or 10/3 for a compressor will work fine. I think what Mr Lazyjack is trying to say is that on a higher amperage service especially, rolled up excess wire yes can cause some voltage drop but not that big of a problem with AC circuits as long as it's not too long (DC is different). Cut your cord at least close to length, and you will have better service. The problem with higher amperage circuits with excess wire coiled up tight together is that it starts to make a transformer under load and can start a fire. I have personally witnessed a 480v temporary feeder to a Motor Control Center catch fire. The "company" that installed that cable had close to 100' of excess 3c 4/0 cable that they coiled up nice & pretty on the deck. Once we started turning heaters on & running motors - loading the gear that roll of cable started smoking and burst into flames as I was walking by. Caught the feeder breaker on fire, smoked out the whole building, and ended up shutting down the whole platform causing everyone to evacuate. Some dipshit roughneck grabbed a water hose and was going to extinguish the fire. Thank God I saw him & stopped him. Anyway..... light weight service not a big deal. Heavier service pay more attention to installation.
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Jimbo1]
#7968177
09/10/20 12:39 PM
|
Joined: Oct 2013
Posts: 1,457
TonyWornick
Pro Tracker
|
Pro Tracker
Joined: Oct 2013
Posts: 1,457 |
Good luck. Haven't used one lately. Most things are now cordless. That was helpful! That's with 98% of his posts.
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Bullfrog]
#7968427
09/10/20 03:14 PM
|
Joined: Dec 2011
Posts: 5,754
Lazyjack
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Dec 2011
Posts: 5,754 |
Lazyjack, you saying it’s better off strung out vs coiled up? or delete the length of unneeded wire for resistance purposes? Trying to wrap my head around that new word. Not resistance, reactance. In a coil of wire with AC current, the induced magnetic fields will act like a choke. It become more prevolent if cord is wadded into a pile. Resistance is relative to DC or pure resistive loads such as a heater or incandescent lamp. Reactance comes in play in motor windings and old school electronics and coils for relays. If you measure motor windings with a meter, you are appling a meter battery power, usualy 9 VDC. In case you are measuing resistance. Using Ohms Law, expected current flow is extremly high. Well, actually, as I sure know, starting amperage is Locked Rotor from 2/3 second. Infact it happens so most meters will not record peak. After rotor beings to spin, reactance causes the amperage to fall. Now I am speaking of AC motors, Not DC.
If the 2nd amendment was written just to include guns for hunting, why is there not an amendment to protect fishing poles?
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Lazyjack]
#7968436
09/10/20 03:22 PM
|
Joined: Jan 2012
Posts: 28,856
TXHOGSLAYER
THF Celebrity
|
THF Celebrity
Joined: Jan 2012
Posts: 28,856 |
Lazyjack, you saying it’s better off strung out vs coiled up? or delete the length of unneeded wire for resistance purposes? Trying to wrap my head around that new word. Not resistance, reactance. In a coil of wire with AC current, the induced magnetic fields will act like a choke. It become more prevolent if cord is wadded into a pile. Resistance is relative to DC or pure resistive loads such as a heater or incandescent lamp. Reactance comes in play in motor windings and old school electronics and coils for relays. If you measure motor windings with a meter, you are appling a meter battery power, usualy 9 VDC. In case you are measuing resistance. Using Ohms Law, expected current flow is extremly high. Well, actually, as I sure know, starting amperage is Locked Rotor from 2/3 second. Infact it happens so most meters will not record peak. After rotor beings to spin, reactance causes the amperage to fall. Now I am speaking of AC motors, Not DC. Learned something new today. Thanks.
LETS GO BRANDON
|
|
|
Re: extension cord needed for 220V compressor?
[Re: skinnerback]
#7968445
09/10/20 03:28 PM
|
Joined: Dec 2011
Posts: 5,754
Lazyjack
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Dec 2011
Posts: 5,754 |
Lazyjack, you saying it’s better off strung out vs coiled up? or delete the length of unneeded wire for resistance purposes? Trying to wrap my head around that new word. Lazyjack made some good points. 12/3 or 10/3 for a compressor will work fine. I think what Mr Lazyjack is trying to say is that on a higher amperage service especially, rolled up excess wire yes can cause some voltage drop but not that big of a problem with AC circuits as long as it's not too long (DC is different). Cut your cord at least close to length, and you will have better service. The problem with higher amperage circuits with excess wire coiled up tight together is that it starts to make a transformer under load and can start a fire. I have personally witnessed a 480v temporary feeder to a Motor Control Center catch fire. The "company" that installed that cable had close to 100' of excess 3c 4/0 cable that they coiled up nice & pretty on the deck. Once we started turning heaters on & running motors - loading the gear that roll of cable started smoking and burst into flames as I was walking by. Caught the feeder breaker on fire, smoked out the whole building, and ended up shutting down the whole platform causing everyone to evacuate. Some dipshit roughneck grabbed a water hose and was going to extinguish the fire. Thank God I saw him & stopped him. Anyway..... light weight service not a big deal. Heavier service pay more attention to installation. Very good post. And an excellent example of reactance. A 10 amp load on 100 feet of 16/3 could have same results. Heavy is relative, like hot or cold, short or tall. In this case, the coiled excess cord causes motor starting issues due high starting amperage. Of course, high starting amperage is relative to running amperage.
If the 2nd amendment was written just to include guns for hunting, why is there not an amendment to protect fishing poles?
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7968482
09/10/20 03:50 PM
|
Joined: Dec 2011
Posts: 5,754
Lazyjack
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Dec 2011
Posts: 5,754 |
Here is good demo. This is low AC voltage, but physics are the same and results simular with high volages provided frequency remains 60 HZ.
If the 2nd amendment was written just to include guns for hunting, why is there not an amendment to protect fishing poles?
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7968487
09/10/20 03:55 PM
|
Joined: Dec 2011
Posts: 5,754
Lazyjack
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Dec 2011
Posts: 5,754 |
I also just reread my original post. I said 15 feet I ment 50 feet. Brain cramp. Guess I was channelling a presidential candidate.
If the 2nd amendment was written just to include guns for hunting, why is there not an amendment to protect fishing poles?
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Lazyjack]
#7968771
09/10/20 07:12 PM
|
Joined: May 2011
Posts: 27,081
skinnerback
THF Celebrity Chef
|
THF Celebrity Chef
Joined: May 2011
Posts: 27,081 |
I also just reread my original post. I said 15 feet I ment 50 feet. Brain cramp. Guess I was channelling a presidential candidate. 
|
|
|
Re: extension cord needed for 220V compressor?
[Re: TXHOGSLAYER]
#7969050
09/10/20 11:36 PM
|
Joined: Jul 2009
Posts: 9,763
Tin Head
OP
THF Trophy Hunter
|
OP
THF Trophy Hunter
Joined: Jul 2009
Posts: 9,763 |
Lazyjack, you saying it’s better off strung out vs coiled up? or delete the length of unneeded wire for resistance purposes? Trying to wrap my head around that new word. Not resistance, reactance. In a coil of wire with AC current, the induced magnetic fields will act like a choke. It become more prevolent if cord is wadded into a pile. Resistance is relative to DC or pure resistive loads such as a heater or incandescent lamp. Reactance comes in play in motor windings and old school electronics and coils for relays. If you measure motor windings with a meter, you are appling a meter battery power, usualy 9 VDC. In case you are measuing resistance. Using Ohms Law, expected current flow is extremly high. Well, actually, as I sure know, starting amperage is Locked Rotor from 2/3 second. Infact it happens so most meters will not record peak. After rotor beings to spin, reactance causes the amperage to fall. Now I am speaking of AC motors, Not DC. Learned something new today. Thanks. As did I , thanks for the help guys
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7975988
09/16/20 01:25 PM
|
Joined: Apr 2009
Posts: 6,025
pdr55
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Apr 2009
Posts: 6,025 |
I would personally leave the compressor close to the power source and get a longer air hose.
If you`re running down my country, man, You`re walking on the fighting side of me. (Merle)
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7980597
09/19/20 10:09 PM
|
Joined: Jan 2011
Posts: 21,367
Bullfrog
THF Celebrity
|
THF Celebrity
Joined: Jan 2011
Posts: 21,367 |
One thing mentioned in this thread that almost everyone could benefit from is Lazyjack said “ohms law”
Good stuff
![[Linked Image]](https://krdesignsco.com/wp-content/uploads/2019/02/pig.gif) Man if I knew what Oxner knows I could throw away what I know
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7980620
09/19/20 10:44 PM
|
Joined: Dec 2008
Posts: 22,630
Cast
THF Celebrity
|
THF Celebrity
Joined: Dec 2008
Posts: 22,630 |
You guys kill me. The OP asks about a simple extension cord. Y’all tell him how to built the ISS. Y’all have talked conductor resistance, inductive reactance, current and heat. Y’all left out capacitance, those wires run side you side you know. Oh! Let’s not forget solar interference and solar flares.
Did anybody answer his question?
He just needs recommendations for a 50’ extension cord for his compressor.
I recommend 10/3 copper rated for outdoor use in a bright color and appropriate connectors. I find it’s usually cheaper to buy a 10/3x50’ extension cord and replace the ends if necessary.
Cast I have a short attention spa
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#7980628
09/19/20 10:53 PM
|
Joined: Nov 2009
Posts: 91,416
bill oxner
THF Celebrity
|
THF Celebrity
Joined: Nov 2009
Posts: 91,416 |
I also use mine for my cheep air compressor.
Quail hunting is like walking into, and out of a beautiful painting all day long. Gene Hill
|
|
|
Re: extension cord needed for 220V compressor?
[Re: pdr55]
#7980697
09/20/20 12:27 AM
|
Joined: Dec 2012
Posts: 11,649
Simple Searcher
THF Celebrity
|
THF Celebrity
Joined: Dec 2012
Posts: 11,649 |
I would personally leave the compressor close to the power source and get a longer air hose.
Best advice on this thread.
![[Linked Image]](https://live.staticflickr.com/4482/37630656532_b3ce0919d1_t.jpg) "Man is still a hunter, still a simple searcher after meat..." Robert C. Ruark
|
|
|
Re: extension cord needed for 220V compressor?
[Re: Tin Head]
#8056513
11/19/20 04:36 PM
|
Joined: Oct 2004
Posts: 39,316
redchevy
THF Celebrity
|
THF Celebrity
Joined: Oct 2004
Posts: 39,316 |
Reading this post reminds me of why my uncle (who is an electrician) told me i know just enough about electricity to be dangerous! lol
Not knowing the complete story or needs, i assume this is just to run it in a shop where the power service isnt right there. I would run some romex