waterline project
#7762112
03/03/20 08:47 PM
|
Joined: Dec 2006
Posts: 1,252
huntindude
OP
Pro Tracker
|
OP
Pro Tracker
Joined: Dec 2006
Posts: 1,252 |
Please critique my plans for my project. Also add additional pieces if it is needed. 1150' downhill 3/4"pvc sch.40. Thank you. Black dots 1. tap into existing 3/4" pvc/add on/off valve (bottom right) 2. 3/4" spigot 3. 3/4" Tee 4. 3/4" spigot 5. 3/4" spigot red dots 1. 3/4" spigot 2. 3/4" spigot
|
|
|
Re: waterline project
[Re: huntindude]
#7762505
03/04/20 05:41 AM
|
Joined: Sep 2007
Posts: 4,294
oldoak2000
Extreme Tracker
|
Extreme Tracker
Joined: Sep 2007
Posts: 4,294 |
1150ft is a loooong run for 3/4” - don’t expect much flow on the ends. How much drop on that hill?
|
|
|
Re: waterline project
[Re: huntindude]
#7762550
03/04/20 12:08 PM
|
Joined: Sep 2004
Posts: 12,420
RedRanger
THF Celebrity
|
THF Celebrity
Joined: Sep 2004
Posts: 12,420 |
way way way way undersized, you gonna kill your volume and pressure
Find a sizing chart they are quit simple to compute you pipe size for water supply
|
|
|
Re: waterline project
[Re: huntindude]
#7762585
03/04/20 01:18 PM
|
Joined: Feb 2020
Posts: 553
AMF
Tracker
|
Tracker
Joined: Feb 2020
Posts: 553 |
Your problem starts at the tie-in to the existing line. 3/4 is sufficient for ONE 3/4 inch spigot up to a hundred feet out. Past that, you need to increase the pipe size by one size every hundred feet. That means the main feeder must be that size also. And in turn, that means the pump must match in size. Further, every added spigot requires the manifold to be increased by one size.
I could lay out the pipe sizes and branches for you, but the main must be large enough at the beginning. You're trying to run a commercial application on an existing residential system. That ain't gonna work.
Oh, and the spigots being downhill are completely irrelevant.
|
|
|
Re: waterline project
[Re: huntindude]
#7762627
03/04/20 02:08 PM
|
Joined: Dec 2006
Posts: 1,252
huntindude
OP
Pro Tracker
|
OP
Pro Tracker
Joined: Dec 2006
Posts: 1,252 |
|
|
|
Re: waterline project
[Re: huntindude]
#7762631
03/04/20 02:11 PM
|
Joined: Dec 2006
Posts: 1,252
huntindude
OP
Pro Tracker
|
OP
Pro Tracker
Joined: Dec 2006
Posts: 1,252 |
Duke, if you don't mind yes i would love a plan. Our house in connected at the "main" that is 1". Both the main line and the counties are both 1". We are at the end of that run on rural water.
|
|
|
Re: waterline project
[Re: huntindude]
#7763754
03/05/20 01:49 PM
|
Joined: Sep 2008
Posts: 6,695
Cochise
THF Trophy Hunter
|
THF Trophy Hunter
Joined: Sep 2008
Posts: 6,695 |
What is the purpose? Just watering trees and grass? Why not just run a pump into the pond and use HDPE or a heavy large enough flexible hose type deal? In a normal year I'd think if you were conservative with your watering you shouldn't put too much of a hurting on the pond.
|
|
|
Re: waterline project
[Re: huntindude]
#7763771
03/05/20 02:12 PM
|
Joined: Feb 2020
Posts: 553
AMF
Tracker
|
Tracker
Joined: Feb 2020
Posts: 553 |
Duke, if you don't mind yes i would love a plan. Our house in connected at the "main" that is 1". Both the main line and the counties are both 1". We are at the end of that run on rural water. I'm not trying to blow you off or pee on your parade, but you need to understand... a one inch line from the source is only enough to feed two 3/4 inch spigots at the same time. Three at the most with 60 PSI pressure. And you're nowhere near close to get enough pressure to push water 1100 feet with multiple spigots. Golf courses use 2 inch mains and 75 PSI pumps to water the fairways. And that's per fairway. The distance you're trying to run is WAY longer than that. You'd have to have a 3 inch tap to the main and a booster pump to make this happen. You're asking for something that can't be done given existing conditions.
|
|
|
Re: waterline project
[Re: huntindude]
#7775132
03/17/20 05:52 PM
|
Joined: Dec 2006
Posts: 1,252
huntindude
OP
Pro Tracker
|
OP
Pro Tracker
Joined: Dec 2006
Posts: 1,252 |
been busy with work to reply to any messages. The over all plan is to use just one spigot at a time. Just watering trees that are little. I'm putting several spigots in just because I guess. My initial plan was to use the pond, but it looks like its on again. I have the pipe for it anyways. Just need to know what solar and size of pump to use. In 2011 we still had plenty of water left in the pond but it was down a lot. We have no power out anywhere except the house. Maybe I'll change that with this project. I'm going to start researching putting a pump in the pond. Is there anyway to regulate a submersible pump? Thanks for all the recommendations folks.
|
|
|
Re: waterline project
[Re: huntindude]
#7775171
03/17/20 06:43 PM
|
Joined: Oct 2004
Posts: 39,542
redchevy
THF Celebrity
|
THF Celebrity
Joined: Oct 2004
Posts: 39,542 |
All the water line posts always end up with a bunch of people telling the op they need to run a huge line. People always seem to spend other peoples money really easy.
If you just want to water trees what you have planned is more than enough. Just put 1200 foot of inch pipe in at my brothers property a few months ago and many said the same things they are telling you here.... his works great, pressure and flow are fine, he is going to build a house on it.
Last edited by redchevy; 03/17/20 06:45 PM.
It's hell eatin em live
|
|
|
Re: waterline project
[Re: huntindude]
#7775279
03/17/20 08:17 PM
|
Joined: Sep 2007
Posts: 4,294
oldoak2000
Extreme Tracker
|
Extreme Tracker
Joined: Sep 2007
Posts: 4,294 |
If you're just 'watering trees' then pressure doesn't matter much - anything would work -even 3/4.
Running a sprinkler needs pressure (&flow) - I once bought 6 100' 3/4" water hoses to try to water a temporary food plot; pressure was too low to get full coverage with just 1 lawn-sprinkler. It 'kinda' worked, but I had to let it run longer and move more often to get full coverage since sprinkler only worked about 75%.
|
|
|
Re: waterline project
[Re: huntindude]
#7783428
03/24/20 11:46 AM
|
Joined: Oct 2010
Posts: 2,870
topwater13
Veteran Tracker
|
Veteran Tracker
Joined: Oct 2010
Posts: 2,870 |
If you are going to put in all that work digging ditches I would go at least 1.5" on the pvc. Friction loss is not your friend here. For 3/4" pvc running 15 gpm at the tie in you will lose 18.4 PSI PER 100'. You will not end up with much at the end. 11/2 pvc at the same volume only lose .7 psi per 100'....yes, that is 7/10 out of 1 psi. Here is your chart. https://www.engineeringtoolbox.com/pvc-pipes-friction-loss-d_802.html
|
|
|
Re: waterline project
[Re: huntindude]
#7783642
03/24/20 03:44 PM
|
Joined: Dec 2006
Posts: 1,252
huntindude
OP
Pro Tracker
|
OP
Pro Tracker
Joined: Dec 2006
Posts: 1,252 |
thanks for all the supplies. I think I will try redchevy advise and just use what I have. Already have the pipe.
|
|
|
Re: waterline project
[Re: huntindude]
#7784548
03/25/20 12:47 PM
|
Joined: Sep 2011
Posts: 3,038
Vern1
Veteran Tracker
|
Veteran Tracker
Joined: Sep 2011
Posts: 3,038 |
It will work just fine if you just need or want water available at those locations. If you plan to irrigate an orchard like most folks seem to think, it simply won't cut it.
If you use 3/4" PVC on a long run make sure it's SCH40 and not the thin crap. If the weather is warmer or hot, make sure to zigzag the PVC in the ditch so when weather cools off and the PVC shrinks, it won't pull apart at the joints.
It's a really simple but somewhat difficult to grasp. With normal pressure, if you put water in one end, it will come out the other end. You will lose volume and pressure but water will still come out.
Get er done before it gets too hot.
Last edited by Vern1; 03/25/20 12:53 PM.
Cheers, Vern1 Texans since The Old 300 in 1824 NRA Lifetime Member
|
|
|
Re: waterline project
[Re: redchevy]
#7784955
03/25/20 05:59 PM
|
Joined: Oct 2010
Posts: 2,870
topwater13
Veteran Tracker
|
Veteran Tracker
Joined: Oct 2010
Posts: 2,870 |
All the water line posts always end up with a bunch of people telling the op they need to run a huge line. People always seem to spend other peoples money really easy.
If you just want to water trees what you have planned is more than enough. Just put 1200 foot of inch pipe in at my brothers property a few months ago and many said the same things they are telling you here.... his works great, pressure and flow are fine, he is going to build a house on it. He asked for critique..... I would be curious as to how many gpm your brother is getting on a 1" line at 1200'.
|
|
|
Re: waterline project
[Re: huntindude]
#7785047
03/25/20 07:15 PM
|
Joined: Jul 2019
Posts: 2,334
rolyat.nosaj
Veteran Tracker
|
Veteran Tracker
Joined: Jul 2019
Posts: 2,334 |
Get a long water hose and move around as needed.
|
|
|
Re: waterline project
[Re: huntindude]
#7822298
04/28/20 04:57 PM
|
Joined: Nov 2017
Posts: 19,271
Biscuit
THF Celebrity
|
THF Celebrity
Joined: Nov 2017
Posts: 19,271 |
PVC is pretty fun to work with
|
|
|
Re: waterline project
[Re: Biscuit]
#7822382
04/28/20 05:53 PM
|
Joined: Nov 2009
Posts: 91,416
bill oxner
THF Celebrity
|
THF Celebrity
Joined: Nov 2009
Posts: 91,416 |
PVC is pretty fun to work with Yep. Just like tinker toys. Great idea of putting a ball [censored] shutoff early and often.
Quail hunting is like walking into, and out of a beautiful painting all day long. Gene Hill
|
|
|
Re: waterline project
[Re: huntindude]
#7822743
04/28/20 10:52 PM
|
Joined: Sep 2012
Posts: 12,865
PMK
THF Celebrity
|
THF Celebrity
Joined: Sep 2012
Posts: 12,865 |
"everyone that lives dies but not everyone who dies lived..."
~PMK~
|
|
|
Re: waterline project
[Re: huntindude]
#7822958
04/29/20 01:45 AM
|
Joined: Aug 2009
Posts: 22,716
BigPig
THF Celebrity
|
THF Celebrity
Joined: Aug 2009
Posts: 22,716 |
It’s a good thing PVC is flexible.
I ran a trencher today, 450 feet in all, took about 3 hours in hard black clay. I opted for the stand on model, makes turns very easy.
|
|
|
Re: waterline project
[Re: huntindude]
#7823310
04/29/20 01:35 PM
|
Joined: Dec 2006
Posts: 1,252
huntindude
OP
Pro Tracker
|
OP
Pro Tracker
Joined: Dec 2006
Posts: 1,252 |
Thanks for the replies. Yes I depended on the flex of the pvc the whole way. I think the hardest part for the trencher was near 2 giant water oaks. 50ft took me about an hour. I planned most of the dig in the open just for this reason, but man do roots grow far from the trees. Another thing i didn't think about was the 3 creosote poles that I used for my faucets. I seem to recall that pigs love these things. Better be careful pigs.
|
|
|
Re: waterline project
[Re: huntindude]
#7823351
04/29/20 02:07 PM
|
Joined: Aug 2009
Posts: 22,716
BigPig
THF Celebrity
|
THF Celebrity
Joined: Aug 2009
Posts: 22,716 |
Trenching a straight line on the smaller machines is hard. The chain grand so much that you can’t give it equal power to each track or it will turn itself to what ever side the chain is on. You did just fine with those cuts
|
|
|