Electrical question at the hunting cabin #7451834 03/06/19 05:28 PM
Joined: Nov 2011
Posts: 662
R
rob valle Offline OP
Tracker
OP Offline
Tracker
R
Joined: Nov 2011
Posts: 662
Hi guys, I need some advice from all you electricians! I have a 16x 24 hunting cabin in the Texas Hill Country. This is how it is currently wired. I have a Honda 2200i inverter generator that we use for power. An extension cord runs from the generator to a male electrical outlet on the outside of the cabin. The power then comes inside through Romex to two electrical outlets and then two light sockets in the rafters. I would like to add an additional outlet on the opposite wall soon. Is this ok? Does there need to be a breaker box? Thanks!


Rob Valle
www.hillcotaxidermy.com
Originally Posted by Texsun
The three things you need in life are a good doctor, lawyer and taxidermist.

Re: Electrical question at the hunting cabin [Re: rob valle] #7451849 03/06/19 05:39 PM
Joined: Dec 2008
Posts: 22,630
Cast Offline
THF Celebrity
Offline
THF Celebrity
Joined: Dec 2008
Posts: 22,630
What’s using power now? Your only concern is overloading the genset. If I was you, I’d get a short 10 gauge crows foot. Male 110 on one end, triple connector on the other end. The kind with power indicator lights build in. Then run crows foot extension cords inside.

If you want to get fancy later, yeah that means actually wiring it.


Cast

[Linked Image]

I have a short attention spa
Re: Electrical question at the hunting cabin [Re: Cast] #7451855 03/06/19 05:42 PM
Joined: Nov 2011
Posts: 662
R
rob valle Offline OP
Tracker
OP Offline
Tracker
R
Joined: Nov 2011
Posts: 662
We use power for the TV, DVD player, and a Keurig Coffee pot. And to charge cell phones. That's about it.


Rob Valle
www.hillcotaxidermy.com
Originally Posted by Texsun
The three things you need in life are a good doctor, lawyer and taxidermist.

Re: Electrical question at the hunting cabin [Re: rob valle] #7451878 03/06/19 06:04 PM
Joined: Dec 2008
Posts: 22,630
Cast Offline
THF Celebrity
Offline
THF Celebrity
Joined: Dec 2008
Posts: 22,630
Originally Posted by rob valle
We use power for the TV, DVD player, and a Keurig Coffee pot. And to charge cell phones. That's about it.


If the genset is 2200 watts, you’re good. You could probably add a small fridge.


Cast

[Linked Image]

I have a short attention spa
Re: Electrical question at the hunting cabin [Re: rob valle] #7451941 03/06/19 07:35 PM
Joined: Oct 2008
Posts: 15,128
Tbar Online Content
THF Celebrity
Online Content
THF Celebrity
Joined: Oct 2008
Posts: 15,128
When we lose power at the farm house my 2200i runs two fridges, TV, cable boxes, and lights. Only time the genset goes to full throttle is when the coffee pot comes on.


Make America Great Again

Re: Electrical question at the hunting cabin [Re: rob valle] #7451953 03/06/19 07:56 PM
Joined: Dec 2011
Posts: 5,815
L
Lazyjack Online Content
THF Trophy Hunter
Online Content
THF Trophy Hunter
L
Joined: Dec 2011
Posts: 5,815
I expect your genny has over current protection for the plugs. The purpose over over current protection (breaker) is to prevent overheating conductors and cords thus preventing fires.

As long as the cords and wire you use are rated for the maximum output of genny you will be ok. No additional breaker needed.

2200i should produce 15 amps of current. It should have 20 amp overprotective device. You should have a 15 amp or greater extension cord to cabin. If you are using a 13 amp cord now, you could be in danger. Probably not, but could be.

Now, please take note, every connection becomes a weak spot. My experience, the male and female ends of extension cords are prone to fail. I often replace them with after market heavy duty connectors.

All your wiring should becable to pass inspection. If a wire or connection is warm to the touch. You have a problem.


If the 2nd amendment was written just to include guns for hunting, why is there not an amendment to protect fishing poles?
Re: Electrical question at the hunting cabin [Re: rob valle] #7452640 03/07/19 02:18 PM
Joined: Jun 2015
Posts: 18,561
Roll-Tide Online Content
THF Celebrity
Online Content
THF Celebrity
Joined: Jun 2015
Posts: 18,561
I am no electrician.

I have a similar setup. 2000 watts is plenty to run what you want. Heat is 1500 watts, AC about 300, fans 20. Lights can be very low with low wattage bulbs.

What I would do is add a few more outlets. Just pigtail and keep running the Romex.
I have 3 light fixtures and 4 outlets. No problems.

You could a a gfci for added protection. I do not think a breaker box is needed.

Re: Electrical question at the hunting cabin [Re: rob valle] #7452655 03/07/19 02:28 PM
Joined: Nov 2011
Posts: 9,835
U
unclebubba Offline
THF Trophy Hunter
Offline
THF Trophy Hunter
U
Joined: Nov 2011
Posts: 9,835
Something nobody has mentioned, How long of an extension chord are you using to plug in the geneerator? The longer the chord, the heavier it needs to be.

Re: Electrical question at the hunting cabin [Re: Lazyjack] #7452993 03/07/19 08:39 PM
Joined: Nov 2011
Posts: 662
R
rob valle Offline OP
Tracker
OP Offline
Tracker
R
Joined: Nov 2011
Posts: 662
Originally Posted by Lazyjack
I expect your genny has over current protection for the plugs. The purpose over over current protection (breaker) is to prevent overheating conductors and cords thus preventing fires.

As long as the cords and wire you use are rated for the maximum output of genny you will be ok. No additional breaker needed.

2200i should produce 15 amps of current. It should have 20 amp overprotective device. You should have a 15 amp or greater extension cord to cabin. If you are using a 13 amp cord now, you could be in danger. Probably not, but could be.

Now, please take note, every connection becomes a weak spot. My experience, the male and female ends of extension cords are prone to fail. I often replace them with after market heavy duty connectors.

All your wiring should becable to pass inspection. If a wire or connection is warm to the touch. You have a problem.



Yes the Honda has the over -current protection feature. The extension cord I'm using is a Rigid 25' heavy duty cord.......I believe it is 12ga but may be 14ga. I'm headed up there on Sunday, I'll be sure to check. Thanks fro the advice! This is what I needed to know.......I don't want the cabin to burn down!


Rob Valle
www.hillcotaxidermy.com
Originally Posted by Texsun
The three things you need in life are a good doctor, lawyer and taxidermist.

Re: Electrical question at the hunting cabin [Re: unclebubba] #7452995 03/07/19 08:40 PM
Joined: Nov 2011
Posts: 662
R
rob valle Offline OP
Tracker
OP Offline
Tracker
R
Joined: Nov 2011
Posts: 662
Originally Posted by unclebubba
Something nobody has mentioned, How long of an extension chord are you using to plug in the geneerator? The longer the chord, the heavier it needs to be.



25'......I will check to make sure it is 15amp this weekend. It is either 12 or 14 gauge, but pretty sure 12ga.


Rob Valle
www.hillcotaxidermy.com
Originally Posted by Texsun
The three things you need in life are a good doctor, lawyer and taxidermist.

Re: Electrical question at the hunting cabin [Re: rob valle] #7453110 03/07/19 11:04 PM
Joined: Aug 2009
Posts: 3,832
T
Texan Til I Die Offline
Extreme Tracker
Offline
Extreme Tracker
T
Joined: Aug 2009
Posts: 3,832
Also check the extension cord for an outdoor rating. Outdoor cords are supposed to be UV stable so they won't deteriorate in the sunlight.


Silver spurs and gold tequila
keep me hanging on.
Pretty girls and old cantinas
give me shelter from the storm.
Re: Electrical question at the hunting cabin [Re: rob valle] #7453788 03/08/19 05:40 PM
Joined: May 2015
Posts: 4,136
D
Dalee7892 Offline
Extreme Tracker
Offline
Extreme Tracker
D
Joined: May 2015
Posts: 4,136
The outside chord should be at least 12 gauge better if 10. Do not use 14 gauge to weak. Protect the plug ends from moisture.

Re: Electrical question at the hunting cabin [Re: rob valle] #7453798 03/08/19 05:48 PM
Joined: Dec 2008
Posts: 22,630
Cast Offline
THF Celebrity
Offline
THF Celebrity
Joined: Dec 2008
Posts: 22,630
What you should do is replace the main cord from the genset with a 10 gauge cord with a crows foot that will reach from inside the cabin, through the wall and plug into the genset. That will eliminate some connections and give you enough oomph to run everything inside without overloading the main cable.


Cast

[Linked Image]

I have a short attention spa
Re: Electrical question at the hunting cabin [Re: rob valle] #7462331 03/19/19 02:23 PM
Joined: Nov 2011
Posts: 662
R
rob valle Offline OP
Tracker
OP Offline
Tracker
R
Joined: Nov 2011
Posts: 662
Ok I checked...the cord from the Honda to the cabin is a Rigid 25' 12 ga 15 amp extension cord.


Rob Valle
www.hillcotaxidermy.com
Originally Posted by Texsun
The three things you need in life are a good doctor, lawyer and taxidermist.

Re: Electrical question at the hunting cabin [Re: rob valle] #7462442 03/19/19 04:15 PM
Joined: Dec 2008
Posts: 22,630
Cast Offline
THF Celebrity
Offline
THF Celebrity
Joined: Dec 2008
Posts: 22,630
That should work fine.


Cast

[Linked Image]