not commercial, will just be residential rates ... and very light usage
"everyone that lives dies but not everyone who dies lived..."
~PMK~
|
|
|
Re: Electric service options & ???
[Re: PMK]
#6881062
09/07/17 03:32 PM
|
Joined: Sep 2012
Posts: 12,822
PMK
OP
THF Celebrity
|
OP
THF Celebrity
Joined: Sep 2012
Posts: 12,822 |
bringing this back up for a few more questions ... Got the pole set, meter loop in place, have all the 110v outlets and lights/switches wired and just ran wires from breaker box below meter thru gray PVC conduit into the building and up to a separate 125 amp breaker box inside. All 110v outlets & lights will be on 4 different 20 amp breakers ... and just need to hook up breakers at both ends and welder outlet (50 amp 220v) which will be on it's own 50 amp breaker in the outside meter box (dedicated wires to welder).
for the welder outlet, I know I hook up two legs of 110v (black & red) but does the third leg get connected to the neutral (white) or common ground (green or bare copper)?
Last edited by PMK; 09/07/17 03:33 PM.
"everyone that lives dies but not everyone who dies lived..."
~PMK~
|
|
|
Re: Electric service options & ???
[Re: PMK]
#6881068
09/07/17 03:36 PM
|
Joined: Sep 2007
Posts: 4,292
oldoak2000
Extreme Tracker
|
Extreme Tracker
Joined: Sep 2007
Posts: 4,292 |
bringing this back up for a few more questions ... Got the pole set, meter loop in place, have all the 110v outlets and lights/switches wired and just ran wires from breaker box below meter thru gray PVC conduit into the building and up to a separate 125 amp breaker box inside. All 110v outlets & lights will be on 4 different 20 amp breakers ... and just need to hook up breakers at both ends and welder outlet (50 amp 220v) which will be on it's own 50 amp breaker in the outside meter box (dedicated wires to welder).
for the welder outlet, I know I hook up two legs of 110v (black & red) but does the third leg get connected to the neutral (white) or common ground (green or bare copper)? Ground! Remember that 'Neutral' actually carries a current (return), and you DONT want any current present to the frame of a machine (ground).
|
|
|
Re: Electric service options & ???
[Re: PMK]
#6881172
09/07/17 05:55 PM
|
Joined: Sep 2012
Posts: 12,822
PMK
OP
THF Celebrity
|
OP
THF Celebrity
Joined: Sep 2012
Posts: 12,822 |
thanks, that's what I was thinking too but hadn't found a clear cut answer in my searches.